Electric Connection - Fairchild T6000 Instrucciones De Instalación, Uso Y Mantenimiento

Tabla de contenido
Idiomas disponibles
  • ES

Idiomas disponibles

Pneumatic Connection
Clean all pipelines to remove dirt and scale before installation.
Apply a minimum amount of pipe compound to the male threads
of the fitting only. Do Not use teflon tape as a sealant. Start
with the third thread back and work away from the end of the fitting
to avoid contaminating the transducer. Install the transducer in
the air line. The inlet and outlet ports are labeled on the ends of
the transducer. Tighten connections securely. Avoid undersized
fittings that will limit the flow through the transducer and cause
pressure drop down stream.
NOTE:
Oil free air is required. Use a filter to remove dirt
and liquid in the air line ahead of the transducer.
If an air line lubricator is used, it MUST be located
downstream to avoid interference with transducer
performance.
The user is responsible for insuring that the
environment in which the unit will be installed and
the operating gas are compatible with the materials
in the transducer.

Electric Connection

Make connections as shown in Figure 9.
CAUTION: Effective November 1997 (DATE CODE NE), the
DIN Connector terminal connections have been changed. The
ground connection has been moved from terminal #3 to the ( )
terminal. When replacing an existing unit, correct wiring on the
mating connector.
MAINTENANCE
To clean the Orifice, use the following procedure:
1.
Shut off the valve that is supplying air to transducer.
It is not necessary to remove the Transducer
from the air line.
2.
Remove the Orifice Assembly from the unit. For
detailed information see Figure 1 "T6000 Calibration
Configuration on page 1.
3.
Clean with alcohol and dry with compressed air.
NOTES:
Parts must be completely dry before reassembling.
If the standard maintenance procedure does not
correct the trouble, install the appropriate Service
Kit below:
16798-1 (3-15, 3-27 & 6-30 psig
Standard Range)
18238-1 (0-30 psig Extended Range)
18239-1 (0-60 psig Extended Range)
18240-1 (0-120 psig Extended Range)
18039-1 (Explosion-Proof Base)
Service Kits also include Gasket, O-Rings, and
Membranes to replace "W" Option product.
TROUBLE-SHOOTING
Table 1. Trouble-Shooting
Problem
No Output
No Output
Low or Improper
Span Adjust
Erratic Operation
WARNING:
Failure of Transducer could result in output
pressure increasing to supply pressure possibly
causing personal injury or damage to equipment.
4
Solution (check)
Supply Pressure
Clogged Orifice
Input Signal
Pneumatic Connections
Zero and Span Adjust
Supply Pressure Low
Output Leakage
DC Signal
Loose Wires or Connections
Liquid in Air Supply
Dirt in Magnet Gap
Tabla de contenido
loading

Tabla de contenido