VIVO-T101
Installation and programming instructions
1
INTRODUCTION
These instructions sheets are valid for VIVO-T101
control boards and must be read along with the VIVO-
M101 instruction manuals.
2
DESCRIPTION
The VIVO-T101 control board is suitable for three-phase
operators and three-phase power supply facilities.
The characteristics of the VIVO-T101 control panels are
similar to VIVO-M101 control panels, with the
following differences:
• A three-phase plate has been added for
connection to the three-phase operators and three-
phase power supply.
• The torque adjustment has been eliminated
(P.M. potentiometer).
• DIP8, DIP9 and DIP12 remain unused (the "soft
stop" function, the "anti-crush" function and the
function for the VULCAN VUS safety device have
been removed).
• Detection
with
photocell
modified, and is now with Photocell in
Opening: only operational during opening, during
which, if enabled, the door stops and closes for 2
seconds; after this, if a key command is received, it
closes.
3
INSTALLATION
Carry out the electrical installation as described in the
VIVO-M101 control board manual, bearing in mind that
the operators and power supply connection must be in
line with the diagram on the following page:
4
PROGRAMMING AND STARTUP
Carry out the programming as described in the VIVO-
M101 control board manual, bearing in mind that DIP8,
DIP9 and DIP12 must always be placed in OFF.
5
FAILURE DIAGNOSIS
Follow the instructions of the VIVO-M101 control board
manual, taking into account fuses F1, F2 and F3 of the
three-phase plate (see figure on the following page).
MSA-102/01
‹
• The functions associated with DIP5 have been
FT2
has
been
Z
O
Bear in mind the safety warnings set out in the
VIVO-M101 manual.
modified.
The
delay
eliminated, and DIP5 is used to control the
behaviour of ST1 and ST2, remaining as follows:
With DIP10=OFF (dead-man mode disabled):
– DIP5=OFF: ST1 starts total opening and ST2
pedestrian opening,
– DIP5=ON: ST1 starts total opening and ST2 total
closing.
With DIP10=ON (dead-man mode enabled):
– DIP5=OFF: dead-man mode in opening and
closing (with ST1 pressed down it opens; with ST2
pressed down it closes),
– DIP5=ON: dead-man mode in closing (with ST1
pressed and released it opens; with ST2 pressed
down it closes).
"Fig. 1 Power supply and operator connections".
IMPORTANT: DIP8, DIP9 and DIP12 must always
be OFF.
English
pulse/ram
contact
is
VIVO-T101 Control board